    EIO Pinout connector to RJ45

    Possible to connect a wideband lc-1 using a female rj45 to male rj45 to eio connector to MPVI pro? 8 pins.. I don't see why not. But the close proximity of the wires might be a problem.

    Also, would it matter if the wire I used was stranded or solid? I have both. I'd be punching down the lc1 wires onto 110-type jacks.

    Or perhaps someone could tell me where to get that eio connector both female and male.

  2. #2
    Senior Tuner S2H's Avatar
    Join Date
    Apr 2005
    Location
    Schexnayder Racing - Arnaudville LA
    Posts
    4,387
    I'm not sure of voltage/amperage limitations of RJ45...
    but I would think its a little much for such small wires...
    -Scott -

  3. #3
    Advanced Tuner
    Join Date
    Jul 2006
    Posts
    403
    Yeah thats what I thought at first but then I saw the lc1 wires.. Not much thicker, if anything.. skinnier. However, there is more shielding on the lc-1 wires.. no doubt about that. 24AWG is some of the utp cat 6 i have. Copper.. I don't know what the gauge and make-up is of the lc-1 wires.. The ones I'd need to convert would be the grounds and the brown signal wire.

    http://en.wikipedia.org/wiki/Power_over_Ethernet

    Electrical Math
    from Ryan Cole

    Wire gauge Ohms per 1000ft
    20 10
    22 16
    24 25
    28 65


    The TIA-568 spec which defines Cat5 (cat 3 as well) specifies that either one shall be no more than 9.38 ohms per 100 meters. Our testing of name brand Cat 5 says more like seven ohms per 100 meters, so 3 ohms per hundred feet is safe and conservative. — Scott Carter

    Ohms Law
    E = IR (Volts = Amps x Resistance)

    We'll say 22 Gauge wire at 250 Ft under a 1 Amp load
    22 Gauge @ 250 Ft = 4 Ohms
    E = 1 x 4 or E = 4 Volts

    So basically you should expect 4 Volts consumed leaving you 8 volts at the AP end.

    Let's do another situation:

    28 Gauge over 50 ft at 2 amps
    28 Guage @ 50 ft = 3 Ohms
    E = 2 x 3 or E = 6 Volts

    So in this case you dissipate half your volts. Could be bad, or if I calculate correctly, possibly worse.

    6 Volts x 2 Amps = 12 Watts dissipated over the wire
    12 Watts / 50 Ft = .24 Watts per foot

    I would not expect that to start a fire outright, but you could use it to keep your pipes from freezing in the winter.

    Using 2 pairs as you did in the example will halve the voltage drop--good idea.